Question Using A Exstention Cord With A Grow Light!

If a grow room does not have an outlet to plug your lights into, can you use an exstention cord to power a 400 watt light?


I am talking about using one of the single outlet, orange kind.
Not the cheap kind that has 3-4 outlets on it.
__________________
I'm here to steal your shit.
dr.micology is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 04-26-09, 13:59   #2 (permalink)
Myco-Monkey
 
ShroomGuerilla's Avatar
 
Join Date: Sep 2007
Posts: 1,300
ShroomGuerilla Level +2000 ProphetShroomGuerilla Level +2000 ProphetShroomGuerilla Level +2000 ProphetShroomGuerilla Level +2000 ProphetShroomGuerilla Level +2000 ProphetShroomGuerilla Level +2000 ProphetShroomGuerilla Level +2000 ProphetShroomGuerilla Level +2000 ProphetShroomGuerilla Level +2000 ProphetShroomGuerilla Level +2000 ProphetShroomGuerilla Level +2000 Prophet
Do you mean you have a 2 prong outlet?
And you are trying to convert
it to a 3 prong via an extension cord?

This can be very very dangerous.
You must make sure that the 2 prong outlet
is grounded, in many cases these ones are not.

This can result in burning your house to the ground...

Or if you are running a cord from another room with
proper grounding, make sure the cord can handle the juice
you are pumping through it, most cords have that info on their package.

Hope i answered your question..

__________________
Revolución motha fucka, you heard of it?
I light the spliff with the flag, while I'm burnin it
ShroomGuerilla is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 04-26-09, 14:01   #3 (permalink)
always aware
 
i patch's Avatar
 
Join Date: Aug 2008
Posts: 291
i patch LEVEL +450 : WEBGODi patch LEVEL +450 : WEBGODi patch LEVEL +450 : WEBGODi patch LEVEL +450 : WEBGODi patch LEVEL +450 : WEBGODi patch LEVEL +450 : WEBGOD
be ok till u get over a thousand watts with 16 awg which is what most laying around house are.. stay safe shorter the better
i patch is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 04-26-09, 14:36   #4 (permalink)
NudistBuddhistRawFoodist
 
pubensis's Avatar
 
Join Date: Dec 2006
Posts: 274
pubensis LEVEL +450 : WEBGODpubensis LEVEL +450 : WEBGODpubensis LEVEL +450 : WEBGODpubensis LEVEL +450 : WEBGODpubensis LEVEL +450 : WEBGODpubensis LEVEL +450 : WEBGODpubensis LEVEL +450 : WEBGOD
I am not qualified to give any advice, but...
Using an extension chord up to 80% of it's load capacity should be moderately safe. Hint: Don't coil excess chord
On a side note, I'm running an air conditioner off an extension chord atm. I think it's an 800 watt air conditioner, and the chord is rated for 1750w
__________________
But for the sake of some little mouthful of flesh, we deprive a soul of the sun and light, and of that proportion of life and time they had been born to enjoy.
pubensis is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 04-26-09, 14:43   #5 (permalink)
Mycophage
 
toadstooll's Avatar
 
Join Date: May 1971
Posts: 173
toadstooll LEVEL +100 - RESPECTEDtoadstooll LEVEL +100 - RESPECTED
Use a 12 gauge ext. cord under 50 Ft. You could get away with 16 gauge but may get a lil hot( would not chance it myself ).
toadstooll is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 04-26-09, 15:01   #6 (permalink)
always aware
 
i patch's Avatar
 
Join Date: Aug 2008
Posts: 291
i patch LEVEL +450 : WEBGODi patch LEVEL +450 : WEBGODi patch LEVEL +450 : WEBGODi patch LEVEL +450 : WEBGODi patch LEVEL +450 : WEBGODi patch LEVEL +450 : WEBGOD
safe to say 75 percent longer u run the more drop u get
i patch is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 04-27-09, 04:19   #7 (permalink)
Smother?
 
roscoe's Avatar
 
Join Date: Oct 2008
Posts: 233
roscoe LEVEL +450 : WEBGODroscoe LEVEL +450 : WEBGODroscoe LEVEL +450 : WEBGODroscoe LEVEL +450 : WEBGODroscoe LEVEL +450 : WEBGODroscoe LEVEL +450 : WEBGODroscoe LEVEL +450 : WEBGOD
i would bet you could load a stock length of extention cord with 80% of its rated load. no more and no longer. the best type is called SO cord and you can get it in any size. I have seen this stuff abused to the MAX! i am an electrician and i use it in my own house. like were i sleep.
__________________
Don't believe everything I think.
roscoe is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 04-27-09, 08:18   #8 (permalink)
Mycotopiate
 
Dank Side Of The Shroom's Avatar
 
Join Date: Oct 2005
Posts: 3,520
Dank Side Of The Shroom LEVEL +1000 : MESSIAHDank Side Of The Shroom LEVEL +1000 : MESSIAHDank Side Of The Shroom LEVEL +1000 : MESSIAHDank Side Of The Shroom LEVEL +1000 : MESSIAHDank Side Of The Shroom LEVEL +1000 : MESSIAHDank Side Of The Shroom LEVEL +1000 : MESSIAHDank Side Of The Shroom LEVEL +1000 : MESSIAHDank Side Of The Shroom LEVEL +1000 : MESSIAHDank Side Of The Shroom LEVEL +1000 : MESSIAH
we used to use em alot. the thick orange ones. if u are using it for a hps a 400 watt id not worry at all. we had 1k going on each of ours last year.
__________________
[SIGPIC][/SIGPIC]
Dank Side Of The Shroom is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 04-27-09, 09:31   #9 (permalink)
Myc
El Jardinero
 
Myc's Avatar
 
Join Date: Apr 2007
Posts: 2,041
Myc has disabled reputation
As mentioned, a properly grounded extension cord is a good idea.
If you don't have an equipement grounding conductor ( a green wire) or the "D" shaped hole in the receptacle outlet face
Try to protect the circuit with a GFCI - Ground Fault Circuit Interruptor

Only load the ciruit to 80% of it's rating capacity

If a 20 amp breaker powers the circuit:
the maximum load on the circuit is limited to

20 amp breaker
20 amps X 80% = 16 amps
16 amps X 120 volts = 1920 watts
Load requires a minimum size # 12 AWG conductors in the extension cord

15 amp breaker
15 amps x 80% = 12 amps
12 amps x 120v = 1440 watts
Load requires a minimum size # 14 AWG conductors in the extension cord

Commercially available HID lighting normally comes with a multi-tap ballast capable of recieving multiple voltage inputs. (120v, 208, 240v, 277v, 480v, and others)
I'm presuming you're using the 120v tap for the ballast.
Myc is online now  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 04-29-09, 15:47   #10 (permalink)
Harvester of Sorrow
 
sandman's Avatar
 
Join Date: Apr 1972
Posts: 1,970
sandman LEVEL +1000 : MESSIAHsandman LEVEL +1000 : MESSIAHsandman LEVEL +1000 : MESSIAHsandman LEVEL +1000 : MESSIAHsandman LEVEL +1000 : MESSIAHsandman LEVEL +1000 : MESSIAHsandman LEVEL +1000 : MESSIAHsandman LEVEL +1000 : MESSIAHsandman LEVEL +1000 : MESSIAHsandman LEVEL +1000 : MESSIAH
whatta you think would happen if you ran 2000 watts on a 20 amp breaker? Its only 80 watts over 80%. Safe?
__________________
Dreams are real. But they are made of viewpoints, of images, of memories and puns and lost hopes
sandman is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 04-30-09, 20:36   #11 (permalink)
Mycophage
 
DrDee's Avatar
 
Join Date: Dec 2008
Posts: 164
DrDee LEVEL +250 : HONORABLEDrDee LEVEL +250 : HONORABLEDrDee LEVEL +250 : HONORABLE
Quote:
Originally Posted by sandman View Post
whatta you think would happen if you ran 2000 watts on a 20 amp breaker? Its only 80 watts over 80%. Safe?
As long as you're not using an extension cord and as long as your breaker doesn't trip, you should be OK. You should have 12 guage wire for that application.
Dee

PS: One little trick that you can use is to have a separate timer for each light and stagger them a few minutes so that the starting surge from both lights doesn't happen at the same time.
DrDee is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 04-30-09, 21:33   #12 (permalink)
Picktish Texas Style...
 
alounacara's Avatar
 
Join Date: Jan 1972
Posts: 2,396
alounacara Level +2000 Prophetalounacara Level +2000 Prophetalounacara Level +2000 Prophetalounacara Level +2000 Prophetalounacara Level +2000 Prophetalounacara Level +2000 Prophetalounacara Level +2000 Prophetalounacara Level +2000 Prophetalounacara Level +2000 Prophetalounacara Level +2000 Prophetalounacara Level +2000 Prophet
Good advice the in rush current is what can make fires
++Rep points
Oops i cannot give you rep points again but somebody else should
__________________
Dont take a tone with me *
So hard to please WDYWFM?
Please do not be the "`Stupes"
alounacara is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Old 05-04-09, 11:44   #13 (permalink)
Mycophiliac
 
zep101's Avatar
 
Join Date: Apr 2009
Posts: 22
zep101 LEVEL +10 - IN GOOD STANDING
a foaf ran 10/3 NMD90 300V from the panel to his room and a 2 pole 20 amp breaker was installed in the panel(abit pricey but he's taking it ALL with him when he moves). BUT he's using 9-42 watt cfl so he's well over the limits. BUT the biggest thing is bonding to ground, like everyones sayin heh. I also am an electrician. making sure that every fixture is bonded and that every polarity is right is the biggest key. just make sure your testers work well enuff. voltage drop is probably the only concern (after everything bonded of course ) but usually you don't see much drop until past 30 meters. but yes, I must stress bond to ground!! if your fixture becomes live, best case scenario you get a gentle poke. worst case, you burn your house down and you with it! good luck! great info in this thread. Myc, your numbers remind me of school. I love it! foaf might have gone overkill with the 10/3 but his room has two circuits(balanced loads aswell) and has plenty of headroom to add more.


BTW voltage at outlets are 117 all around the house...thats the VD that you can't fix cause it's most likely right off the poll
zep101 is offline  
Digg this Post!Add Post to del.icio.usBookmark Post in TechnoratiFurl this Post!
Reply With Quote
Reply

Bookmarks

Tags
cord, exstention, grow, light

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off



All times are GMT -5. The time now is 09:34.

Mycotopia Web Forums


Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.
SEO by vBSEO 3.2.0


All trademarks are © their respective owners, all other content is © Mycotopia 2000/2008
Site Designed and Hosted By | Zen Media Studios




[Output: 107.17 Kb. compressed to 100.78 Kb. by saving 6.39 Kb. (5.97%)]